Hello,

I am running a thermal simulation of a building in an urban context using Viper.

These are the runtime messages:

Batch file launched successfully.
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_3", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_4", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_5", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_6", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_7", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_8", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_9", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_10", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_11", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_12", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_13", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_14", in Zone="ZONE1".
** Warning ** GetVertices: Floor is not oriented correctly! Tilt angle=[90.0], should be near 180, Surface="ZONE1_FACE_15", in Zone="ZONE1".
** Severe ** ComputeIntSolarAbsorpFactors: Solar distribution model is set to place solar gains on the zone floor,
** Warning ** DetermineShadowingCombinations: There are 1 surfaces which are receiving surfaces and are non-convex.
************* EnergyPlus Completed Successfully-- 14 Warning; 1 Severe Errors; Elapsed Time=00hr 01min 26.84sec

The surfaces listed as "floor" are actually the vertical facades of the building, with all normals facing outwards. Why does EnergyPlus consider them as floors?

I think the severe message could be related to the facades issue, while I am not sure of understanding the last warning. Does it refer to the simulated building or to the shading objects?

I attach a the dxf output file of the simulation. It seems that the slab of the building has not been taken into account, even if it was attached to the zone beep input of the GH component.

I would be very grateful for any help you could give me.

Giuseppe

Tags: thermal, viper

Views: 205

Attachments:

Reply to This

Replies to This Discussion

After several attempts, I managed to solve all the problems of my model.
The were all caused by non-convex surfaces used for the slab. Apparently, Energy Plus was able to correctly triangulate a non-convex surface used the rooftop, but not the one of the slab. This caused the facades to be considered as floors.